Introduction
Classification of Fire and Construction Hazards
Planning for Fire Protection
Fire Safety Design
Fire Detection and Signaling Devices
Fire Alarm Systems

Fire Suppression Systems
Automatic Sprinkler Systems
Smoke Controls
Engineer Дата: 08.10.2017, в 11:55 | Сообщение №2
Engineer

Старожил
Пользователь №: 2125
Сообщений: 375

Introduction
A fire protection system includes: devices, wiring, piping, equipment, and controls to detect fire or smoke, to actuate signal, and to suppress the fire or smoke.
Objectives of fire protection:

Primary objectives: to save lives and protect property.
Secondary objective: to minimize interruptions of service due to a fire.

Current trends in building design and modern lifestyles contributing to serious fire hazards:

High-rise buildings: Buildings become taller and more densely situated.

Architectural design: Larger areas and open spaces. Less separation walls.

Controlled indoor environment: Constructed of fixed glass windows instead of operable windows in order to mechanically control temperature, humidity and air quality and to minimize a stack effect.

Increased use of combustible materials: Furnishings, equipment, and decorative finishes made of materials such as plastic and synthetics are a source of toxic gas and smoke during a fire.

Classification of Fire and Construction Hazards
Classification of Fires (according to NFPA, U.S.A.)

Class A
Fires of ordinary combustible materials such as wood, cloth, paper, rubber, and many plastics.

Class B
Fires in flammable liquids, oils, greases, tar, oil-base paints, lacquers, and flammable
gases.

Fires that involve energized electrical equipment. Extinguishing medium must not be a
conductor of electricity.
Class D
Fires of combustible metals, such as magnesium, titanium, zirconium, sodium, lithium, and potassium.

Classification of Hazards

Light (low) hazard: Locations where the total amount of Class A combustible materials is minor.
Ordinary (moderate) hazard: Locations where Class A combustibles and Class B flammables are present in greater amounts than expected under light hazard occupancies.
Extra (high) hazard: Locations with large quantities of highly combustible materials

Type 1 construction is the most fire-resistant. Walls, partitions, ceilings, floors, roofs, structural system, and exit envelopes shall all be constructed of noncombustible material having at least the minimum fire resistance rating specified in the fire code.
Use or Occupancy (Construction Type)

Group A: Assembly. Occupied by more than 1000 people (A-1), less than 1000 people , and other situations (A-3, A-4, and A-5).
Group B: Business. Used for offices, professions or service-type transactions.
Group E: Educational. Elementary schools (E-1, E-2), daycare (E-3).
Group F: Factory. Moderate hazard (F-1), low Hazard (F-2).
Group H: Hazard. Group H-1 through H-7, depending on the hazardous material being handled or stored.
Group I: Institutional. Nurseries, hospital, nursing homes (I-1), others (I-2, I-3).
Group M: Mercantile- display, storage and sale of merchandise.
Group R: Residential
Hotels, motels, or boarding houses (R-1)
Multifamily dwellings (R-2)
One-family or two family dwellings (R-3) child care (R-4)
Group S: Storage
Moderate hazard (S-1)
Low hazard (S-1)
Repair garage(S-3)
Open parking garage (S-4)
Aircraft (S-5)
Group U: Utility. Buildings not covered by the above groups

Planning for Fire Protection

Step 1: Detection
The presence of a fire is detected manually or automatically.
Step 2: Signaling
The building’s management, its occupants and the fire department are notified of the presence of the fire.

Step 3: Suppression
Manual or automatic fire suppression equipment and systems are used to extinguish the fire and remove the smoke.

3A (Initial effort): Potable and manual firefighting equipment, such as fire extinguishers, fans, and a first-aid fire hose, are used to extinguish the fire and to remove smoke by dilution or exhaustion.

3B (Main effort): Fire suppression systems, such as automatic sprinklers, fire hoses, and other systems, are used to extinguish the fire. Smoke control systems are activated to remove or confine the spread of smoke.
3C (Last Effort):
The fire department takes over the firefighting effort when all previous efforts are ineffective
Engineer Дата: 08.10.2017, в 11:56 | Сообщение №3
Engineer

Старожил
Пользователь №: 2125
Сообщений: 375

Fire Safety Design

Fire-resistant construction
Smoke controls
Length of travel

Means of egress

Exit enclosures

Adequate lighting

Vertical openings

Vertical transportation

Coordination with mechanical and electrical system
Compliance with code requirements for specific use

Fire Detection and Signaling Devices
Manual Alarm Station
Bells, gongs, and flashing lights are manually activated by a switch.
To avoid accidental operation of the switch, the station is usually designed so that a person must break a glass panel or glass rod or must perform other preliminary actions before the alarm can be operated

Thermal Detectors
Thermal detectors are temperature-activated sensors to initiate an alarm.
Fixed-temperature type: This sensor consists of normally open contact held by bimetallic elements that will close the contacts when the ambient temperature reaches a fixed setting. The setting is generally designed for operation at 57℃, 88 ℃, or 94℃.
Rate-of-rise (ROR) type: This sensor reacts to the rate at which the temperature rises. It contains a sealed but slightly vented air chamber which expands quickly when the temperature near the device rises quickly. When the air chamber expands faster than it can be vented, electrical contacts attached to the chamber begin to close and thus initiate an alarm.
Combination type: This device reacts to both a fixed temperature and a rate of rise.

Smoke Detectors
Smoke detectors are quicker to respond than thermal detectors.
Photoelectric type
Ionization type

Photoelectric type
This type operates on the principle of the scattering of light. Photoelectric detectors
detect the presence of visible particles (larger than 3 microns) in the air. Inside the detector, there is a light emitting diode (LED) that directs a narrow beam of infrared light across the detection chamber. When smoke or particles enter the chamber, the infrared light beam is scattered. A photodiode or photo detector, usually placed 90 degrees to the beam, will sense the scattered infrared light and when a preset amount of light is detected, the alarm will sound. Photoelectric detectors are not as sensitive and are designed to detect cool or slow-moving (smoldering) fires that produce a lot of smoke.

Ionization type
This type operates on the principle of changing conductivity of air within the detector
chamber. The ionization detector uses a small amount of radioactive material to make the air within a sensing chamber conduct electricity. When smoke particles or combustion gases enter the sensing chamber they interfere with the conduction of electricity, reducing the current and triggering an alarm. The ionization detector can detect even invisible combustion gases produced by an open flame and will therefore respond slightly faster to an open flame fire than a photo-electric detector.

Flame Detectors

Flame detectors are used to detect the direct radiation of a flame in the visible, infrared, and ultraviolet ranges of the spectrum.
Flame detectors are used mostly in industrial processes for the protection of combustion equipment. Thermal or smoke detectors would be unreliable and generate false alarms in
these environment.
There are four basic types:

Infrared detector
Ultraviolet detector
Photoelectric detector
flame flicker detector

Fire Alarm Systems
Fire alarm systems are an integral part of a fire protection plan. They are basically electrical systems that are specially designed to announce the presence of fire or smoke. They are not intended to suppressor extinguish a fire.

Fire Suppression Systems
Fire suppression is achieved by cooling the combustible material to below its ignition temperature or by preventing oxygen from reacting with the combustible material.
Fire suppression system must be designed by considering the class of fire and the type of building occupancy.
Fire suppression system may be classified in several ways.
According to the fire suppression medium – water, foam, chemical, gas, etc.
According to the action of the device – a portable extinguisher, standpipe and hose, automatic sprinkler, etc.
According to the method of operation of the device – manual or automatic.
Engineer Дата: 08.10.2017, в 11:56 | Сообщение №4
Engineer

Старожил
Пользователь №: 2125
Сообщений: 375

Water Supply
Water is the universal firefighting medium.
It is readily available in large quantities and, in general, is more economical than any other firefighting medium.

For fire protection purposes, the water supply should be separated from a building’s domestic water system, even though the two are connected to the same public water
main.

Portable Fire Extinguishers
Portable fire extinguishers are used as the first line of fire protection.
They are normally pre-charged with water or chemicals and are hand-operated.

Standpipe-and– Hose Systems (Standpipe systems)
Standpipe systems consist of piping, valves, hose connections, and nozzles to provide streams of water for fire suppression.
Wet system

Wet system
A "wet" standpipe is filled with water and is pressurized at all times.
Whenever the system is activated, water will charge into the connected hose immediately.
Wet standpipes can be used by building occupants.

Dry system
A “Dry” standpipe is NOT filled with water.
The intakes of dry standpipes are usually located near a road or driveway so that a fire engine can supply water to the system.
This system can be used only by firefighters.
Regulations in many countries require that standpipe systems be charged by hoses from two different pump trucks, which can be accomplished by using both sides of a Siamese connection.

Other Fire Suppression Systems

Foam systems

Foam systems are most effective for Class B fires caused by liquid, oil, grease, paint, etc.
The foam is made by generators, which mix water with detergent or other chemicals to produce as much as 1000 gallons of foam for each gallon of water.
This systems suppress fire by separating the fuel from the air (oxygen).

Other Fire Suppression Systems
Gaseous fire suppression systems
- Gaseous systems are most effective for Class C fires
caused by electrical equipment.
- All these gases are stored in liquid state under high
pressure.
- There are three varieties in agent gases:
The carbon dioxide: CO2
Halogenated gas : fluorine, chlorine, bromine, or iodine
Atmospheric gas: mixture of argon, carbon dioxide, and
nitrogen. The gas mixture is nontoxic, with zero ozone depletion potential (ODP) and zero global-warming potential (GWP).

H-cylinder canisters containing argon gas for use in extinguishing fire in a server room, without damaging equipment
Dry Chemicals
Dry chemicals are used especially for Class D fires caused by combustible metals.

Examples of such metals include sodium, titanium, magnesium, potassium, uranium, lithium, plutonium, and calcium. Magnesium and titanium fires are common. When one of these combustible metals ignites, it can easily and rapidly spread to surrounding ordinary combustible materials.

Most of the dry chemicals contain bicarbonates, chlorides, phosphates, and other proprietary compounds.

The use of water should be avoided on burning metals, since hot metal extracts oxygen from water, promotes combustion, and at the same time liberates hydrogen, which ignites readil

Automatic Sprinkler Systems
Automatic sprinkler systems are integrated fire suppression systems consisting of a water supply and a network of pipes, sprinkler heads, and other components to provide automatic fire suppression in areas of a building.

This system is the most effective for suppressing a Class A fires in buildings containing ordinary combustible materials, such as wood, paper, and plastics.

The design and installation of the system are strictly regulated by insurance companies and in accordance with fire codes.

Sprinklers

The major component of an automatic sprinkler system is the sprinkler, which discharge water in specific pattern for extinguishing or controlling a fire.

A sprinkler head consists of three major components:

Nozzle
Heat detector: Fusible link type / Frangible bulb type
Water spray pattern deflector

The fusible link type of heat detector is constructed of a “eutectic alloy”
which melt at a specific temperature rather than gradually softening. When the link temperature reaches its melting point, the link is pulled apart by the water pressure and opens nozzle

The frangible bulb type of detector contains a glass bulb partially filled with a liquid that expands with temperature. At the rated temperature, the liquid will shatter the bulb and open the nozzle.
The temperature rating of heat detectors is divided into seven groups.

Sprinklers are color-coded for ease of identification.

Types of Automatic Sprinkler Systems (Wet-pipe and Dry-pipe)
Wet-pipe system
et-pipe sprinkler systems employ automatic sprinklers attached to a piping system
containing water and connected to a water supply so that water discharges immediately from sprinklers opened by a fire.
This type is the most reliable and simple of all sprinkler systems since no equipment other
Only those sprinklers which have been operated by heat over the fire will discharge

Dry-pipe system

Dry-pipe sprinkler systems employ automatic sprinkler attached to a piping system containing air or nitrogen under pressure.

When sprinklers are open by a fire, the gas is released and the dry pipe valve is open by the water pressure. The water then flows into the piping system and discharges only from those sprinklers which have been open by heat over the fire.

Dry-pipe systems are installed in lieu of wet-pipe systems where piping is subject to freezing

Smoke Controls
Smoke is always present when there is a building fire.

The degree of smoke generated depends on the combustible material of the fire.

Fire from wood and paper generates relatively light smoke, whereas fire from plastic or synthetic materials generates heavy, toxic smoke.
Engineer Дата: 08.10.2017, в 11:57 | Сообщение №5
Engineer

Старожил
Пользователь №: 2125
Сообщений: 375

Stack Effect
Smoke spreads in a building primarily
Hot air: makes the smoke rise owing
to its lower density (stack effect).
Pressure differences in building:
cause air to migrate throughout the building.
Stack effect is more serious in cold weather
than in hot weather, since the temperature differential between the outdoors and the

Pressure Control

Air flows only when there is a pressure difference between two areas. The flow is from the area of higher pressure to the area of low pressure.

If the fire area is maintained at a relatively low pressure by exhausting, then air containing smoke will not flow easily to the other areas in the building.

Some common control practices are as follows:

Local exhaust
Pressure sandwich
Compartmentation
Stair pressurization
Sealing of all penetrations
Pressurizing elevator shaft

Local Exhaust

Exhaust by fans or relief by venting at the floor where fire is started will create low pressure in the fire zone, causing air in the other zones to rush in and thus confine the smoke
Pressure Sandwich

By the proper control of air supply, return, and exhaust, smoke at the fire zone will have less chance to migrate to the other zones.

Compartmentation

The building is divided into two or three vertical compartments as if they were separated buildings stacked on top of each other.

This practice is used only in buildings taller than about 50 stories.

Stair Pressurization

The stairways are the major means of egress from a building.

If positive pressure is maintained in stairways by a stair pressurization fan, smoke will not
migrate into the stairways.

Sealing of All Penetrations

All openings for piping, ducts, or structural members in or out of the fire partitions, walls, floors, and shafts are paths of smoke.

These openings should be sealed and caulked.

Pressure Control in the Elevator Shaft

Maintaining a positive pressure in the elevator shaft is particularly important for elevators designed for use by firefighters and the physically disabled people.

Вы не можете ответить в тему анонимно, пожалуйста, войдите или зарегистрируйтесь!


Forums ©
Легализация короткоствольного огнестрельного оружия

ЗА
ПРОТИВ


Результаты
Другие опросы

Всего голосов: 172
Комментарии: 6
Copyright © Проект Подряд - Работа для архитекторов и инженеров, 2009-2013. Все права защищены.
Powered by SLAED CMS © 2005-2007 SLAED. All rights reserved.